It is not unusual to have a reading of this magnitude on a TT system and providing it is below 200 ohms and 30 millamp rcds are fitted this will be ok
You must ensure that the RCD's are properly tested and the quartely test label is fitted
Baso
Thanks Baso, thought it might something fairly simple.
the saint
Copyright (c) 2007. The Building Experience Ltd. Registered England and Wales. No: 6245614. All rights reserved
Terms & Conditions
As a newly qualified sparks, I recently completed a rewire. When carrying out the verification test I had a reading of 58.4 ohms. The system is a TT system. Any one give advice please.